User: wlr, Location: Ohio
Asked on: Wednesday, February 9, 2011 at 6:54 pm EST
Answered on: Tuesday, May 14, 2024 at 1:23 am EDT
Question: We are adding a electric range and dryer to an existing residential unit. When using the Optional Electric Load Calculation, are the range and dryer part of the "general calculated load" (100% of the 1st 10kva plus 40% of the remainder)? See NEC 220.82B. Or are the range and dryer calculated as 100% of the nameplate just like an a/c unit? Please reference a NEC article.
Range and dryer are calculated as 100% of the nameplate rating.NEC 220.82(B) states: "For the optional method of calculating the service load of a one-family dwelling or of an individual unit of a two-family dwelling with electric cooking and/or clothes drying appliances served by 120/240-volt, single-phase service, the following calculations shall be permitted: (1) General calculated load plus kitchen and laundry loads"Kitchen and laundry loads are calculated at 100% of the nameplate rating, as per NEC 220.