Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sizing of Supply Side bonding jumper

User: mshields, Location: Boston, MA

Asked on: Wednesday, February 9, 2011 at 7:03 pm EST
Answered on: Tuesday, May 14, 2024 at 1:23 am EDT

Question: Just reviewing 2011 code changes, specifically 250.102(C) which has to do with the sizing of the Supply side bonding jumper. Here's my question. If your comming off, say a 45kVA delta wye transformer, the ground conductor to your 208V panel is now referred to as a "supply side bonding jumper" correct. And the size of that conductor is to be based on 250.66.Was this cable size, prior to this change, based on Table 250-122.

Yes, prior to the 2011 code change, the size of the ground conductor coming off the transformer's secondary side to the panel was based on Table 250-122. Flag for review

Previous Question Next Question