Question: Just reviewing 2011 code changes, specifically 250.102(C) which has to do with the sizing of the Supply side bonding jumper. Here's my question. If your comming off, say a 45kVA delta wye transformer, the ground conductor to your 208V panel is now referred to as a "supply side bonding jumper" correct. And the size of that conductor is to be based on 250.66.Was this cable size, prior to this change, based on Table 250-122.
Yes, prior to the 2011 code change, the size of the ground conductor coming off the transformer's secondary side to the panel was based on Table 250-122. Flag for review