Topic: Junction box study guide question

User: jkpyke, Location: 3 Hr 2 Min from Winged Horses

Asked on: Wednesday, February 9, 2011 at 11:48 pm EST
Answered on: Tuesday, May 14, 2024 at 1:24 am EDT

Question: I was using a study guide, and it came to a junction box question. I don't understand how they came up with this answer.A junction box has 2 trade size 3 raceways entering on the left side. The conductors from one of these leave the top of the box in a trade size 3 raceway in an angle pull. The conductors from the second trade size 3 on the left wall are pulled straight through one of the trade size 2 raceways on the right. Two trade size 2 raceways enter from the right side and two trade size 3 raceways enter from the bottom. All raceways entering the bottom are angle pulls.Now the first question states what is the distance from the left wall to the right wall? Which would be 8 x 3 = 24. I get that and agree with that.But the second question reads what is the distance from the bottom wall to the top wall? They give an answer of 21. Should it not be 24 also going by 314.28(A)?

The answer to the second question is indeed 24 inches, using the same formula in NEC 314.28(A). The formula states that the distance between the highest point and lowest point on the enclosure interior is not to exceed the sum of the diameters of all raceways entering within 6 inches.In this case, the highest point is the top of the trade size 3 raceway that leaves the top of the box, and the lowest point is the bottom of any of the trade size 3 raceways that enter from the bottom. There are two trade size 3 raceways entering from the bottom, so the sum of their diameters would be 6 inches.Therefore, the distance from the bottom wall to the top wall should be:6 inches (diameter of 2 trade size 3 raceways) + 18 inches (diameter of 6 trade size 2 raceways) = 24 inchesSo, the answer should be 24 inches. Flag for review

Previous Question Next Question