User: ocoee, Location: Golden Co
Asked on: Thursday, February 10, 2011 at 9:27 am EST
Answered on: Tuesday, May 14, 2024 at 1:24 am EDT
Question: I would like to use SER as a "feeder" to a sub panel from my 150 amp service equipment. I would like to install a 150 amp sub panel.Seems like I remember being told once I must use the 60 degree column of 310-16The actual insulation on the conductors is XHHW-2 Can I use the 75 degree column?Must I use 4/0 for this application?Thank you---G
Conductor Sizing
Per Table 310.16, you must use the 60 degrees Celsius column for XHHW-2 conductors when used in a wet location, which is typical for outdoor applications. However, as this is a feeder to a subpanel and not a branch circuit, you can use the 75 degrees Celsius column per NEC 310.15(B)(2).
Conductor Selection
According to Table 310.16, for a 150-amp feeder using XHHW-2 conductors in a 75 degrees Celsius column, you need to use at least
3/0 conductors.
Conclusion:
Based on the information provided, you can use the 75 degrees Celsius column and 3/0 XHHW-2 conductors for the SER feeder to the 150-amp subpanel. However, it's always best to consult with a licensed electrician for specific installation guidance and to ensure compliance with local codes and standards. Flag for review