Topic: 220.14 (k)

User: stevenje, Location: Yachats Oregon

Asked on: Thursday, February 10, 2011 at 3:17 pm EST
Answered on: Tuesday, May 14, 2024 at 1:25 am EDT

Question: If you have an office area in a building (@ warehouse, service center...) that is not in an office building, can you use the Demand Factors Table 220.44 for the receptacle load?220.14(K) states Banks and Office Buildings, not office areas of other types of buildings. Any thoughts on this?

220.14(K) Demands for Office Buildings was withdrawn from the 2014 NEC. It no longer exists.

The general receptacle load calculation method as contained in 220.44 can be used only in commercial occupancies, as defined in Article 100.The Demand Factors given in Table 220.44 for Receptacle Load Only can only be applied to the lighting and receptacle receptacle load in Guestrooms of Hotels and Motels only.The OP was referring to an office space in a building that was not an "office building". Table 220.44 cannot be used for general receptacle loads in that instance.General purpose branch circuits feeding receptacles in commercial spaces such as those mentioned in the OP must be calculated according to the loads determined per Article 220, Part III. Flag for review