Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sizing for1-20HP Motor

User: wmeek, Location: Texas

Asked on: Thursday, February 10, 2011 at 3:19 pm EST
Answered on: Tuesday, May 14, 2024 at 1:25 am EDT

Question: I have a 20HP motor with a nameplate of 230V ,3phase, 47 amps. So to size the breaker feeding the motor, you use Table 430-250 for the amperage for 20hp, and mutiply times the values given in 430-52 (In this case we are using a breaker) of 250%. That would be 54A x 250% = 135A. So can I go down to a 125A breaker to feed this motor and be to code. Also the conductor size is based on 430-50 current values X 125% = 67.5a. So the conductor would need to be a #4. The motor is approx. 100' from the panel. So with all this said will this be code compliant for this motor installation.

Using a 125A breaker to feed a 20HP motor with a nameplate of 230V, 3-phase, 47 amps would not be code compliant based on the provided calculations.

Breaker Sizing

According to Table 430-250, the full-load current for a 20HP, 3-phase motor at 230V is 54A. Per Table 430-52, the maximum circuit breaker amperage allowed for a motor circuit is 125% of the full-load current for a breaker with a maximum rating of 100A or less. Therefore, the required breaker amperage is 54A x 125% = 67.5A. A 125A breaker would exceed the allowable circuit breaker amperage, which is not code compliant.

Conductor Sizing

According to Table 430-50, the continuous load current for a 20HP, 3-phase motor at 230V is 67.5A. Per Table 310-16, a #4 AWG copper conductor has an allowable ampacity of 75A. Since the calculated continuous load current (67.5A) is less than the allowable ampacity of the #4 AWG conductor (75A), a #4 AWG conductor would be sufficient.

Additional Considerations:
The motor is 100' from the panel, which may require additional voltage drop calculations to ensure proper motor operation.* Without additional information on the motor, it is not possible to determine if this installation meets the requirements of Article 430, Part IX (Motor Circuits, Feeders, and Branch Circuits).Therefore, it is recommended to use a 60A breaker and verify that the motor is operating properly and meets all applicable code requirements. Flag for review

Previous Question Next Question