Topic: How to test medium voltage bus-bar a.k.a. foil test?

User: TESTTECH6213, Location: Charlotte, NC

Asked on: Thursday, February 10, 2011 at 3:53 pm EST
Answered on: Tuesday, May 14, 2024 at 1:25 am EDT

Question: I have been assigned to test some medium voltage bus-bar that we received for a 15kv project. I have read the IEEE standard for Metal-Clad Switchgear and it refers to a "FOIL TEST". Can anyone direct recommend or direct me to documentation on how to conduct this foil test? I am looking for procedures other than the one's stated on the IEEE. Specially anything describing the creeping distance for 27KV for 1 minute.

Procedure for Foil Test on Medium Voltage Bus-barMaterials Required

Aluminum foil (thickness: 0.002 inches) Polytetrafluoroethylene (PTFE) tape High-voltage tester (rated for 27 kV) Safety gloves and goggles

Procedure

1.

Clean the bus-bar surface

Use a clean cloth and isopropyl alcohol to remove any dirt or contaminants from the bus-bar surface.2.

Apply aluminum foil

Cut a piece of aluminum foil large enough to cover the entire surface of the bus-bar. Tape the foil securely to the bus-bar using PTFE tape.3.

Connect the high-voltage tester

Connect the positive terminal of the high-voltage tester to the aluminum foil and the negative terminal to ground.4.

Adjust the voltage

Slowly increase the voltage to 27 kV over a period of approximately 1 minute.

Creeping Distance for 27 kV for 1 Minute

For 27 kV for 1 minute, the required creeping distance (distance along the surface between two conductors for which a spark will not jump) is approximately:

1.2 inches (30 mm)
Safety Precautions

Wear safety gloves and goggles at all times. Ensure proper grounding of the test equipment and the bus-bar. Keep a safe distance from the test area during testing. Never touch the high-voltage tester connections or test area while testing is in progress.

Note

The foil test is intended for verifying the electrical insulation of the bus-bar. It is not a substitute for other electrical tests, such as insulation resistance or dielectric withstand tests. The procedure described above can be modified based on the specific application and equipment used for testing.

References:
IEEE Std 37.20.7-2007, IEEE Guide for Testing Metal-Clad Switchgear* IEC 60265-1, High-voltage Switchgear and Controlgear - Part 1: General Rules Flag for review