Question: I believe that you can pull a smaller neutral wire on a service to a residence but I can't seem to find how to size it in the code book. Help anyone? Its a 200 amp service and I am pricing out copper and aluminum for the owner.
2020 NEC: Sizing of Neutral Line for 200 Amp ServiceArticle 220.67 states that the size of the neutral line shall not be less than the size calculated by either
Method 1: 70% Rule
For a service rated 100 amperes or more, the neutral line shall be not less than 70% of the ampacity of the largest ungrounded conductor.
Method 2: Load Calculations The neutral line shall be sized to carry the maximum net unbalanced current, as calculated in accordance with Article 220.60.
For a 200 Amp Service
Method 1: 70% Rule Largest ungrounded conductor for a 200 amp service is typically 3 AWG copper (250 kcmil aluminum). Neutral line size: 70% of 3 AWG = 2 AWG copper (400 kcmil aluminum)Method 2: Load Calculations Determine the maximum net unbalanced current based on the load conditions. For a typical residential service with balanced loads, the neutral current would be negligible. Therefore, a neutral line size of 2 AWG copper (400 kcmil aluminum) would likely be sufficient.
Note: The neutral line should be of the same material as the ungrounded conductors. The neutral line must be continuous and not spliced throughout its length.* This sizing guidance assumes a single-phase service. For three-phase services, the neutral line sizing may differ. Flag for review