User: Nsmith, Location: Ann Arbor, Michigan
Asked on: Thursday, February 10, 2011 at 7:54 pm EST
Answered on: Tuesday, May 14, 2024 at 1:27 am EDT
Question: A Phase monitor was not pulling in today on a piece of equipment so I was checking the voltage. There is a transformer that knocks the Voltage down from 480 to 240 Delta Delta Config. I have attached an image of the winding setup for the transformer to this post. The 480 is wired and tests as follows.PrimH1 with 1 285 to GndH2 with 2 265 to GndH3 with 3 262 to GndSecX1 115 to GndX2 119 to GndX3 191 to GndX6 is not connected.I spoke with Sola HD on the phone and they told me I need to have X6 to Gnd I told them I need 240 Phoundase to Phase and If I connect X6 that will give me 120. Speaking to another person they told me I need to have any one of the phases grounded or it will not test right.I cant up load the pic so its on page 9 of 10 electrical connection 28
Understanding the Transformer Configuration
The transformer configuration you described is a 480V Delta-Delta transformer with one open leg (X6). This means that the primary windings are connected in a delta configuration, with H1-H2, H2-H3, and H1-H3 forming three closed loops. The secondary windings are also connected in a delta configuration, with X1-X2, X2-X3, and X1-X3 forming three closed loops.
Impact of Grounding
Grounding one of the secondary phases (X1, X2, or X3) is essential for proper voltage measurement and operation of the phase monitor. The neutral point (X6) of the secondary winding is typically grounded to provide a reference potential for the three phases. If the neutral point is not grounded, the voltage readings taken between the phases will not be accurate, and the phase monitor may not function correctly.
Verification of Voltage Readings
To verify the voltage readings, you should connect a voltmeter between each pair of secondary phases (X1-X2, X2-X3, and X1-X3). The readings should be approximately equal to: X1-X2: 240V X2-X3: 240V X1-X3: 240VIf the voltage readings are significantly different from these values, it may indicate an issue with the transformer or the wiring.
Open Leg (X6)
The open leg (X6) on the secondary winding is typically used to connect a ground reference point. However, in your case, you need 240V phase-to-phase voltage. Therefore, leaving X6 open is acceptable as long as one of the other secondary phases is grounded.
Conclusion
Based on the information provided: Grounding one of the secondary phases (X1, X2, or X3) is essential for proper voltage measurement and operation of the phase monitor. The open leg (X6) can remain open if you do not require it for grounding. The voltage readings between the secondary phases should be approximately 240V. Flag for review