User: Ken 6789, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)
Asked on: Friday, February 11, 2011 at 12:11 am EST
Answered on: Tuesday, May 14, 2024 at 1:27 am EDT
Question: Just out of curiosity, On a multi-family house with two meters and two service panels, how would you terminate the gec from H2o and grd rods to the two tenant panels? I assume it is ok to terminate a gec to the neutral bar of panel #1 and run a jumper gec of same size to the neutral bar of panel #2 and terminate the H2o gec to the neutral bar of panel #2. I don't believe a gec from the grd rods and H2o line can be bonded together to a common point outside of the panels then to each panel. I'm just interested in how others would terminate the gec in this example. Thanks.
Termination of GEC to Two Tenant PanelsMethod 1: Separate GEC Runs to Neutral Bars H2O GEC
Terminate to the neutral bar of Panel #1.
Grd Rod GEC
Terminate to the neutral bar of Panel #2.
Jumper GEC
Run a jumper conductor of the same size as the H2O GEC from the neutral bar of Panel #1 to the neutral bar of Panel #2.
Method 2: Common GEC Bonding Point GEC Bonding Point
Create a common bonding point (e.g., a grounding lug) outside of the panels.
H2O GEC
Terminate to the grounding lug.
Grd Rod GEC
Terminate to the grounding lug.
GEC to Neutral Bars
Run GEC conductors from the grounding lug to the neutral bars of both Panel #1 and Panel #2.
Additional Considerations
Ensure that all GEC conductors are of the correct size as per NEC requirements (usually #6 AWG for service sizes up to 400 amps). Use approved connectors and grounding clamps for all terminations. Label all GEC conductors clearly to indicate their source.
Justification:
While the GEC from the H2O line and grd rods can be bonded together at a common point outside of the panels, some jurisdictions may require separate GEC runs to the neutral bars for each panel. This provides additional redundancy in case of a fault or damage to one of the GEC paths.By following either of the methods described, the GEC will properly connect the grounding system to the neutral bars of both tenant panels, ensuring safety and compliance with electrical codes. Flag for review