Question: A job I am researching has a garage with a common wall to a sink.Would like to locate 2 panelboards in the garage, on the common wall with a sink (sink is on the opposite side of the wall).In reviewing NEC 110.26 F 1 it appears that if the plumbing for the sink is confined by wall studs with the panelboards on the opposite sides of the wall studs I am OK.| panelboard | sink plumbing | panelboard |Can EMT from one of the panelboards penetrate a wall stud into the sink plumbing cavity? Is the EMT part of the "equipment"?
Yes, you can locate two panelboards in the garage, on the common wall with a sink, if the plumbing for the sink is confined by wall studs with the panelboards on the opposite sides of the wall studs.However, the EMT from one of the panelboards cannot penetrate a wall stud into the sink plumbing cavity. The plumbing is considered "wet" and the EMT is considered "equipment"; therefore, they cannot be in the same cavity without being separated by a barrier. Flag for review