Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MV Cable installed in C Type Conduit Bodies

User: csully12, Location: Illinois

Asked on: Friday, February 11, 2011 at 8:52 am EST
Answered on: Tuesday, May 14, 2024 at 1:28 am EDT

Question: I am working on a design build project that the contractor has installed C type conduit bodies in a 4" rigid conduit run. The conduit will have 3-1/0 15kV cables installed. I don't like the idea of the conduit bodies being used but need to find a viloation of some sort to get them to remove it and change to a pullbox. Has anyone run into this or have any input on this type of installation? I know its a fill factor violation but I wanted to list as many as I could.Thanks in advance for any input.

Potential Violations



National Electrical Code (NEC)



Article 300.15(E)
: "Conductors in conduit shall not be spliced or terminated within the conduit or in conduit bodies." (Exception: Push-in connectors for #4 AWG or smaller conductors in a 1/2-inch conduit)National Electrical Safety Code (NESC)



Rule 91B

"Conduit bodies shall not be used where the joined conductors consist of two or more conductors of 500 kcmil or larger."

Manufacturer's Instructions

Consult the manufacturer's instructions for the conduit bodies. They may prohibit the installation of cables of this size or quantity in the conduit bodies.

Other Considerations



Fill Factor

The presence of the conduit bodies significantly reduces the available fill area within the conduit for the cables. This can lead to overheating and damage to the cables.

Accessibility

Conduit bodies can make it difficult to access the cables for inspection, maintenance, or replacement.


Mechanical Stress

The sharp edges and bends in the conduit bodies can damage the cables when installed or pulled.

Grounding

Conduit bodies must be properly grounded to maintain continuity of the grounding path for the cables.


Reliability

Conduit bodies introduce additional potential failure points in the conduit system, which can compromise the reliability of the electrical installation.

Recommendations:
Request the contractor to remove the conduit bodies and install a pullbox instead. Clearly communicate the specific code and manufacturer violations that justify the removal of the conduit bodies.* Document all discussions and agreements with the contractor in writing. Flag for review

Previous Question Next Question