User: tonyjz, Location: Saint Joseph, Mo.
Asked on: Friday, February 11, 2011 at 11:32 am EST
Answered on: Tuesday, May 14, 2024 at 1:28 am EDT
Question: Good day. I have completed a ICC webinar and the instructor was doing wires calculations. He stated thatyou may decrease your wire size by using 90c conductor on 75c equipment. I was taught and checked in the code book this can't be done. If all equipment is rated 75c you stay with that column. Have i missed somethig??Example; using a #8 not a #6 as the 8 is rated higher at 90c.
You are correct.
According to the National Electrical Code (NEC), you cannot reduce the wire size below the ampacity value for the equipment it is supplying, even if the conductor is rated for a higher temperature.In your example, if all the equipment is rated for 75°C, you must use the ampacity values from the 75°C column in Table 310.16 of the NEC to determine the appropriate wire size. Using a #8 wire, which is rated for 90°C, would not be permissible.The instructor's statement is incorrect and should not be followed. Flag for review