User: howardrichman, Location: 3 Hr 2 Min from Winged Horses
Asked on: Friday, February 11, 2011 at 1:05 pm EST
Answered on: Tuesday, May 14, 2024 at 1:28 am EDT
Question: If I'm to use larger (10GU) feeder to an A/C condensor, then use 12 conductor wire from the disconnect to a A/C condensor; is that allowable w/o fusing the whip to the condensor w/20A fuses if I'm using a 20A HACR breaker feeding the #10 feeder? Does a tap rule apply in this case. There is to be an inspection.Thanks;HR...
Yes, that is allowable without fusing the whip to the condenser with 20A fuses.Explanation
The National Electrical Code (NEC) allows for tapping smaller conductors from larger conductors without overcurrent protection under certain conditions. This is known as the "tap rule."In this case, the following conditions are met: The main feeder (10 AWG) is protected by a 20A HACR breaker. The tapped conductor (12 AWG) is not more than 10 feet long.* The tapped conductor is used to supply a single piece of equipment (the A/C condenser).Therefore, the tap rule applies, and you do not need to fuse the whip to the condenser.
Note: The maximum length of the tap conductor is determined by the ampacity of the tapped conductor and the overcurrent protection of the main feeder. In this case, the maximum length of the 12 AWG tap conductor is 9 feet. Flag for review