Topic: Ground Fault sesor ( detector )

User: Ralphie, Location: Hart mi

Asked on: Friday, February 11, 2011 at 3:49 pm EST
Answered on: Tuesday, May 14, 2024 at 1:28 am EDT

Question: Does the NEC require ground fault detector on a 480 volt system.

Yes, a ground fault detector is required on a 480 volt system. 230.95 states: Ground-fault protection for equipment shall be provided for solidly grounded wye electrical systems of more than 150 volts to ground but not exceeding 600 volts phase-to-phase for each service, feeder, and branch circuit that is not a part of a grounded system. Flag for review