Topic: highline voltage distance from petroleum tank

User: GEA, Location: Mission Viejo, CA

Asked on: Friday, February 11, 2011 at 4:39 pm EST
Answered on: Tuesday, May 14, 2024 at 1:29 am EDT

Question: A local power company wants to put a high voltage (12,470 VAC) overhead line within fifteen feet of an oil/gas petroleum tank. The content of the tank is very flammable. The working rule of thumb is not to put a highline any closer to a tank than the length of the pole, plus ten feet. What document or article would clarify the proper distance a highline pole should be from a hazardous area tank? Thank you.

National Electrical Safety Code (NESC)

The National Electrical Safety Code (NESC) provides guidelines for the design, construction, and operation of electrical systems, including overhead lines.

Specific Requirement

Section 250.18(B)(6) of the NESC states:> "Overhead lines operating at over 600 volts should not be installed within the following distances of a surface containing a flammable liquid or flammable gas:> - For overhead lines up to and including 15 kV, the distance should be not less than a distance equal to the length of the pole, plus 10 feet."Therefore, the minimum distance from the 12,470 VAC highline pole to the petroleum tank should be:

Pole length + 10 feet = 15 feet
Additional Resources: [NESC Section 250.18(B)(6)](https://www.nescstandards.org/sections/section-250-overhead-lines/) [NESC Website](https://www.nescstandards.org/) Flag for review