Topic: Apartment Building Going To Electric Baseboard Heat

User: Walters Powerhouse, Location: Foothills of NC

Asked on: Friday, February 11, 2011 at 6:35 pm EST
Answered on: Tuesday, May 14, 2024 at 1:29 am EDT

Question: I wanted to get some different opinions on installing electric baseboard heat in a apartment building with 4 apartments. two apartments are larger 770 square feet each. The other two apartments are smaller and only have about 477 square feet. My city inspector request 10watts per sq foot with electric baseboard heat. Each apartment is ran off a 100 amp Westinghouse 8 space Panel board. It says on the cover accepts breakers br,bo,bq,brwh,brsw and something that looks like gfcb which I'm not sure about. the two small apartments have 3 spaces left in the panel board. One of the two large apartments panel's is full and the other apartment has only two spaces left.So with the small apartments i came up with 477 feet x 10 =47704770/240=19.875 amps x 1.25 (for heat)=24.84amps so one 30 amp cir for each of the small apartments installed entirely of 10# wire.For the large apartments i came up with 40.10amp I assume that would they would take two 30 amp cir to run all the electric baseboard heat in each of the apartments. I'm having trouble with determining if i can install piggy back breakers in these panels to get out of doing a upgrade on the service.Thanks for any help you can throw my way.

Electrical Calculations Small apartments: 4770 watts / 240 volts = 19.875 amps Large apartments: 7700 watts / 240 volts = 32.083 ampsPanel Board ConsiderationsSmall Apartments

The panel has 3 spaces left, which is sufficient for a 30-amp circuit (1 breaker + 1 neutral bar). You can install a 30-amp circuit with 10# wire for each small apartment.

Large Apartments

One panel is full, so you will need to perform an upgrade to add more spaces. The other panel has 2 spaces left, which is not sufficient for two 30-amp circuits (2 breakers + 2 neutral bars).

Piggyback Breakers
The panel board accepts BR, BO, BQ, BRWH, BRSW, and GF (ground fault circuit interrupter) breakers. Piggyback breakers, also known as tandem breakers, can be installed if the panel board is rated for them. However, the Westinghouse panel board you described does not specify whether it allows piggyback breakers.

Recommendations
Upgrade the panel board for the large apartments

This is necessary to provide sufficient space for the required circuits.

Install 30-amp circuits with 10# wire for the small apartments

This will meet the code requirements and provide adequate heating capacity.


Contact an electrician

To determine if the panel board allows piggyback breakers and to perform the upgrade safely and to code.

Note:


It is crucial to follow the manufacturer's instructions and local electrical codes when working with electrical systems. Always consult with a qualified electrician for any major electrical work. Flag for review

Previous Question Next Question