Question: I wanted to get some different opinions on installing electric baseboard heat in a apartment building with 4 apartments. two apartments are larger 770 square feet each. The other two apartments are smaller and only have about 477 square feet. My city inspector request 10watts per sq foot with electric baseboard heat. Each apartment is ran off a 100 amp Westinghouse 8 space Panel board. It says on the cover accepts breakers br,bo,bq,brwh,brsw and something that looks like gfcb which I'm not sure about. the two small apartments have 3 spaces left in the panel board. One of the two large apartments panel's is full and the other apartment has only two spaces left.So with the small apartments i came up with 477 feet x 10 =47704770/240=19.875 amps x 1.25 (for heat)=24.84amps so one 30 amp cir for each of the small apartments installed entirely of 10# wire.For the large apartments i came up with 40.10amp I assume that would they would take two 30 amp cir to run all the electric baseboard heat in each of the apartments. I'm having trouble with determining if i can install piggy back breakers in these panels to get out of doing a upgrade on the service.
Electric Baseboard Heat Calculations Small Apartments
477 sq ft x 10 watts/sq ft = 4,770 watts 4,770 watts / 240 volts = 19.875 amps Circuit Amperage: 19.875 amps x 1.25 (diversity factor for heat) = 24.84 amps Circuit Requirement: One 30-amp circuit with #10 wire
Large Apartments
770 sq ft x 10 watts/sq ft = 7,700 watts 7,700 watts / 240 volts = 32.08 amps Circuit Amperage: 32.08 amps x 1.25 (diversity factor for heat) = 40.10 amps
Panel Board Analysis Small Apartments
Three spaces remaining in the panel board One 30-amp circuit can fit in the remaining three spaces
Large Apartments
Only two spaces remaining in the panel board Two 30-amp circuits cannot fit in the remaining two spaces
Piggyback Breakers Some panels have the option to install piggyback breakers, which allow two circuits to share the same physical space. However, based on the panel board specifications provided, it does not mention allowing piggyback breakers. Therefore, it is not possible to install piggyback breakers in these panels.
Conclusion The small apartments can have electric baseboard heat installed with one 30-amp circuit each. The large apartments require two 30-amp circuits each, which cannot be accommodated in the existing panel boards.* An upgrade to the service and panel boards may be necessary to install electric baseboard heat in the large apartments. Flag for review