Topic: Oversizing conductor to the first receptacle

User: X-27, Location: Durango, CO, 10 h 20 min from the winged horses.

Asked on: Saturday, February 12, 2011 at 11:29 pm EST
Answered on: Tuesday, May 14, 2024 at 1:31 am EDT

Question: Sometimes the panelboard can't be as close as we would like. On a 20 amp circuit, I am thinking of running #10 AWG to the first receptacle in a room. Then from that first receptacle running #12 AWG to the remaining receptacles.The specs for this receptacle says it's terminal accommodation is 14-10 AWG. So I don't even have to make pigtails. Is this a reasonable option?(The HO doesn't want to run his stereo on 119.9 Volts.)

Yes, your proposed setup is a reasonable option for extending a 20-amp circuit to additional receptacles in a room. Here are the details: #10 AWG to the First Receptacle

Running #10 AWG wire from the panelboard to the first receptacle in the room is acceptable because it is the same gauge as the circuit breaker. This ensures that the wire can handle the full 20 amps of current.


#12 AWG from First Receptacle to Remaining Receptacles

Using #12 AWG wire to connect the remaining receptacles from the first receptacle is also acceptable. While #12 AWG wire is typically used for 15-amp circuits, it can also be used for 20-amp circuits if the length of the wire run is short.

Receptacle Terminal Accommodation

The receptacle you have chosen has terminal accommodation for 14-10 AWG wire, which means you can directly connect both #10 AWG and #12 AWG wires to the terminals without using pigtails. This simplifies the wiring process.


Voltage Drop:
The concern about voltage drop is valid. Running #12 AWG wire for a short distance from the first receptacle to the remaining receptacles should not result in significant voltage drop. However, it's worth noting that the voltage drop will be slightly higher than if you were to use #10 AWG wire throughout the entire circuit.Overall, your proposed setup is a reasonable option for extending a 20-amp circuit while minimizing voltage drop. It is also compliant with the National Electrical Code (NEC) and will provide a safe and reliable electrical system for the room. Flag for review