Topic: working space

User: Big Guns, Location: NE Nebraska

Asked on: Sunday, February 13, 2011 at 9:24 am EST
Answered on: Tuesday, May 14, 2024 at 1:31 am EDT

Question: In an electrical closet with electrical panels voltage 208 and the room is conrete all around but only 24 inches deep, if a door is in stalled in front of panel do you still need 40 inches of clearence Table 110.26 (A) (1) condition 2

Yes, regardless of the size or depth of the electrical closet, 40 inches of clearance is still required in front of any electrical panel where the voltage exceeds 120 volts, including 208 volts. Flag for review