Question: The code says "Legally required standby systems overcurrent devices shall be selectively coordinated with all supply side overcurrent protective devices." My question is regarding other overcurrent devices, not in the standby path, but may affect the standby supply. For example, suppose you have a main breaker that feeds everything. Are you required to coordinate all breakers in the system - or just the ones in the standby path, up to the main breaker?
The referenced code only requires that "Legally required standby systems overcurrent devices shall be selectively coordinated with all supply side overcurrent protective devices." This means that all overcurrent devices in the standby path, up to and including the main breaker, must be selectively coordinated. Overcurrent devices that are not in the standby path are not required to be coordinated with the standby system.In your example, you have a main breaker that feeds everything. The main breaker is not in the standby path, so it does not need to be coordinated with the standby system. However, all of the breakers in the standby path, up to and including the main breaker, must be selectively coordinated.This is because the standby system must be able to operate even if the main breaker trips. If the breakers in the standby path are not selectively coordinated, then a fault in a non-standby circuit could trip the main breaker and cause the standby system to lose power. Flag for review