Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Romex stuff

User: leftcoastsparky, Location: Tennessee

Asked on: Sunday, February 13, 2011 at 1:49 pm EST
Answered on: Tuesday, May 14, 2024 at 1:32 am EDT

Question: Used to be you could use common sense in running romex through 2x4 studs and plates. (ex. 4-14/2 through a 1-1/4" hole.) Now, around here it is 2 wires, no exceptions. I know thats not set in stone and there are exceptions. What are they? TY

Exceptions to Two-Wire Rule for Romex Through 2x4 Studs and Plates



Romex with Bonding Jumper

Romex cables that have a bonding jumper (green or bare copper wire) installed can pass through a single 1-1/4" hole.


Pancake Boxes

When using pancake boxes that are less than 1-1/4" deep, up to three 14 AWG wires or two 12 AWG wires can pass through a single hole.

Combination Plates

If using a combination plate that has a hole for both a switch and a receptacle, up to four 14 AWG wires can pass through a single hole.


Fire-Rated 2x4 Studs

Fire-rated 2x4 studs typically have a thicker centerboard, allowing for more wires to pass through. In some cases, up to three 12 AWG wires may be allowed through a single hole.

Knife Plates

When using knife plates that cut a slot in the stud, the number of wires allowed depends on the size of the slot. Consult the plate manufacturer for specific guidelines.

Additional Considerations:
Always follow local electrical codes and manufacturer's specifications. Use Romex with proper voltage and temperature ratings. Protect wires from sharp edges or other damage. Ensure wires are not overstuffed or pinched. Keep wires separated from other cables, such as coaxial or speaker wires. Flag for review

Previous Question Next Question