User: ROKETRIK, Location: Illinois
Asked on: Monday, February 14, 2011 at 10:26 am EST
Answered on: Tuesday, May 14, 2024 at 1:34 am EDT
Question: We have an existing 3-phase 208v service with an on premises outdoor transformer. X0 at the transformer is bonded to ground (a counterpoise) as required by 250.24(a)(2). There was no main bonding jumper installed at the service disconnect, a 300 amp distribution panel. The service lateral is run in RGC and the grounding conductor run in it and connected to X0 as well. Neither the ground bar or the neutral bar in the service are connected to the counterpoise.One side of the discussion maintains that no bonding jumper is needed at the service disconnect because of the connection at the transformer and because installing one would put the grounding conductor in parallel with the grounded conductor thereby putting objectionable current on the grounding conductor. The other side maintains there should be a bonding jumper installed in the panel per 250.24 (1) and it should connect to the counterpoise.As I look at the illustration in the handbook, Exhibit 250.7, I notice that this example shows the service lateral as underground cable which would not have a separate grounding conductor and so there is no direct connection between ground at the service and ground at the transformer and I wonder if this is the situation that the Code committee had in mind and if that should make a difference in this case.
According to the 2020 NEC
250.24(A)(2) requires a grounding conductor to be connected to the grounding electrode system at the service equipment. 250.24(C)(1) requires a main bonding jumper to be installed at the service equipment to connect the neutral bar to the grounding electrode system.
In this case
The grounding conductor is connected to the counterpoise at the transformer. There is no main bonding jumper at the service disconnect.
Therefore, the service disconnect is not properly bonded to the grounding electrode system.The statement that installing a bonding jumper would put the grounding conductor in parallel with the grounded conductor is incorrect. The grounding conductor is already in parallel with the grounded conductor at the transformer. Installing a bonding jumper at the service disconnect would simply ensure that the equipment ground is also connected to the grounding electrode system.
The fact that the service lateral is run in RGC does not make a difference in this case.* The RGC contains a grounding conductor that is intended to be connected to the grounding electrode system at both the transformer and the service disconnect.
Conclusion:
A main bonding jumper should be installed at the service disconnect to connect the neutral bar to the counterpoise (grounding electrode system). This is required by the NEC to ensure that the service equipment is properly bonded to the grounding electrode system. Flag for review