Question: Hello,I am currently installing a 208v delta to 480v wye transformer to supply a milling machine. I have done my homework but I am second guessing myself on this so I could use another opinion.I have calculated my primary breaker to be 156 amps which I will raise up to 175a.I will be using 2/0 as feedersMy secondary will be rated @ 70 amps and protected by a fused disconnect.I will be using #6My grounding will be a #6Are my conductors overkilled?This particular machine only needs 440 volts and needs a 40 amp circuit, the machine is also internally fused at 40 amps.I will go from my equipment ground on the machine, to my disconnect then to the case on the transformer. I will bond the XO of my secondary side to the case of the transformer then building steel (right next to the transformer).one of my concerns is when I pipe my primary to the transformer will this become another path to ground?I have seriously confused myself.....maybe im just getting oldany help would be appreciated
Conductors
Primary (2/0 AWG)
Generally adequate for the calculated primary current of 175 amps.
Secondary (No. 6 AWG)
May be oversized for a 40-amp circuit. Typically, No. 8 AWG would be sufficient.
Grounding (No. 6 AWG)
Adequate for a 40-amp circuit.
Secondary Protection
Fused Disconnect
A 70-amp fused disconnect is appropriate for a 40-amp circuit, providing ample overcurrent protection.
Grounding
Equipment Ground
Proper grounding is crucial. Connect the equipment ground from the machine to the disconnect, then to the transformer case.
Neutral Grounding
Bond the X0 (neutral) terminal of the secondary to the transformer case, then to the building steel. This provides a low-impedance path for fault currents.
Primary Piping to Transformer
Grounding Path
The metal conduit or piping used to route the primary wires from the disconnect to the transformer can indeed become an additional path to ground.
Isolation
Ensure that the conduit is properly isolated from other metal parts of the building to prevent parallel grounding paths. Use non-metallic bushings where the conduit enters the transformer enclosure.
Additional Considerations
Machine Voltage
Verify that the transformer is rated for the correct machine voltage (440 volts).
Machine Fusing
Since the machine is internally fused at 40 amps, ensure that the secondary circuit protection is coordinated with the machine fusing.
Voltage Drop
Calculate the voltage drop in the primary and secondary conductors to ensure that the machine receives the proper voltage.
Short-Circuit Protection
Assess the potential short-circuit current at the transformer location and ensure adequate short-circuit protection is provided.
Recommended Modifications: Consider using No. 8 AWG conductors for the secondary. Ensure proper isolation of the primary conduit to prevent additional grounding paths.* Verify the transformer voltage rating and coordinate the secondary protection with the machine fusing. Flag for review