Question: Why are we sizing EGC's the same for a circuits with an available fault current of 65ka and 10ka? Worst case scenario figured into 250.122?Thanks.
No, it is not the same.The size of an equipment grounding conductor (EGC) is determined based on the available fault current at the location where it is installed. The higher the available fault current, the larger the EGC must be to safely carry the fault current back to the source.The NEC Table 250.122 provides the minimum size of EGCs for different circuit ampacities and available fault currents. For example, for a circuit with an available fault current of 65kA, the minimum size of the EGC is 6 AWG copper or 4 AWG aluminum. For a circuit with an available fault current of 10kA, the minimum size of the EGC is 10 AWG copper or 8 AWG aluminum.The NEC also requires that the EGC be sized to carry the maximum fault current that can flow through the circuit. This is because the EGC is the path for the fault current to return to the source, and if it is not sized correctly, it could overheat and cause a fire. Flag for review