Topic: mounting raceway on ductwork

User: Ohmboy, Location: NE Arkansas

Asked on: Tuesday, February 15, 2011 at 7:42 am EST
Answered on: Tuesday, May 14, 2024 at 1:36 am EDT

Question: We did an awsome job with the conduit work in this electric room.The HVAC installer came in behind us and installed the heating and cooling system for this room.The unit has a power venter enclosed in the ductwork which requires 24v to operate.They ran LFMC to the venter and attached the raceway and the junction box to the outside of the ductwork associated with the unit.To me this is a no-no but I cant provide a code reference to back it up.Does anyone have any input?Thanks

NEC 392.11(A) Securing and Supporting"Electrical equipment shall be securely fastened in place."NEC 300.11(1) Listing"Electrical equipment listed for the use shall be installed and used in accordance with any instructions included in the listing."NEC 300.18(2) Fire Resistance of Electrical Equipment"Electrical equipment shall be of the fireresistant type where required by other articles of this Code."Application to Your Situation

The HVAC installer's use of LFMC (liquid-tight flexible metal conduit) is concerning because it is not a listed method for securing electrical equipment to ductwork. The raceway and junction box are attached to the outside of the ductwork, which may not provide the necessary support or protection from heat and fire. The power venter requires 24V to operate, which may not be provided by the NEC-compliant wiring methods used for the other electrical equipment in the room.

Recommendations:
Contact the manufacturer of the HVAC unit to determine the approved methods for securing the power venter and associated raceways. Use listed methods for securing electrical equipment to ductwork, such as metal straps or brackets. Ensure that the raceway and junction box are constructed of fireresistant materials and are installed with appropriate clearances from the ductwork.* If 24V power is required for the power venter, provide a dedicated circuit with the appropriate overcurrent protection and wiring methods. Flag for review