User: wyboy, Location: Logan, Utah
Asked on: Tuesday, February 15, 2011 at 10:37 am EST
Answered on: Tuesday, May 14, 2024 at 1:36 am EDT
Question: 250.52(A) (2)How can building steel be connected to a concrete encased electrode (rebar). The code just says connect. Is rebar tied to J bolts ?connected?? Also if a water pipe comes up at one end of the building and the service is at the other, and the service is large enough to require a 3/0 WP grounding electrode conductor, can you still carry the electrode back on the rebar? Would you have to use a 3/0 UFER in that case?
Connection of Building Steel to Rebar250.52(A)(2) requires building steel to be bonded to concrete encased electrodes (rebar). This is typically accomplished by welding rebar to J-bolts, which are embedded in the concrete slab. The J-bolts are then connected to the building steel with bolts or other approved methods.
Use of Rebar as a Grounding Electrode Conductor
Yes, rebar can be used as a grounding electrode conductor (GEC) as long as it meets the requirements of 250.56(A). However, the GEC must be sized in accordance with Table 250.
66. For a 3/0 WP service, a 3/0 UFER would be required.In the scenario you described, where the water pipe is at one end of the building and the service is at the other, you would need to install the 3/0 UFER from the service to the water pipe. The rebar could then be used to bond the building steel to the UFER at the water pipe end.
Additional Considerations The rebar used as a GEC must be clean and free of paint or other non-conductive coatings. The connection points between the rebar and the UFER or J-bolts must be securely tightened.* The entire grounding system should be inspected and tested regularly to ensure proper functionality. Flag for review