User: chase15, Location: Los Angeles, Ca
Asked on: Tuesday, February 15, 2011 at 11:36 am EST
Answered on: Tuesday, May 14, 2024 at 1:36 am EDT
Question: 3/0 XHHW is rated 200 amps @75c.4/0 XHHW is rated 230 amps @75c.per NEC 240.4B & 240.6 is it allowable to use 3/0 on a 225A ckt bkr? (for a non-continuous rated load).my colleague says you cannot use 3/0 since there is an OCD rating of 200A so 3/0 cannot exceed this established OCD rating. the argument is that the next OCD rating of 225A must use 4/0 since 3/0 cannot go up to the next higher rating because it is locked in at 200A.this is a big deal since there is an existing 2 inch conduit that can be utilized and the smaller 3/0 conductor would help the installation. (this feeder is not continuously rated.)
According to NEC 240.4B and 240.6
The ampacity of a conductor must be equal to or greater than the current rating of the overcurrent device (OCD) protecting it. The OCD rating must not exceed the ampacity of the conductor it protects.In this case: The 3/0 XHHW conductor is rated 200 amps at 75°C. The OCD rating is 225 amps.
Therefore, according to NEC 240.4B and 240.6, it is
not allowable to use a 3/0 XHHW conductor on a 225 amp circuit breaker.Reasoning
The OCD rating exceeds the ampacity of the conductor. The OCD rating must not exceed the ampacity of the conductor.
Your colleague's argument is correct. The 3/0 XHHW conductor cannot be used on a 225 amp circuit breaker because the OCD rating would exceed the ampacity of the conductor. In order to use a 225 amp OCD rating, a 4/0 XHHW conductor would be required, as it is rated for 230 amps at 75°C.
Note: The size of the conduit is not a factor in determining the allowable conductor ampacity. The conduit size is determined based on the number and size of conductors installed within it. Flag for review