User: chase15, Location: Fl
Asked on: Tuesday, February 15, 2011 at 11:37 am EST
Answered on: Tuesday, May 14, 2024 at 1:36 am EDT
Question: 3/0 XHHW is rated 200 amps @75c.4/0 XHHW is rated 230 amps @75c.per NEC 240.4B & 240.6 is it allowable to use 3/0 on a 225A ckt bkr? (for a non-continuous rated load).my colleague says you cannot use 3/0 since there is an OCD rating of 200A so 3/0 cannot exceed this established OCD rating. the argument is that the next OCD rating of 225A must use 4/0 since 3/0 cannot go up to the next higher rating because it is locked in at 200A.this is a big deal since there is an existing 2 inch conduit that can be utilized and the smaller 3/0 conductor would help the installation. (this feeder is not continuously rated.)
NEC 240.4B states that "The ampacity of conductors shall not exceed the rated ampacity of the overcurrent protective device used to protect them."NEC 240.6 states that "Where the ampacity of a conductor differs from the ampacity of the circuit protective device, the ampacity of the circuit protective device shall not exceed the ampacity of the conductor."In this case, the ampacity of the 3/0 XHHW conductor is 200 amps at 75°C, and the ampacity of the 225A circuit breaker is 225 amps. Therefore, the ampacity of the circuit breaker exceeds the ampacity of the conductor, which is not allowed by NEC 240.4B.
Answer:
Therefore, it is not allowable to use 3/0 XHHW conductor on a 225A circuit breaker, even for a non-continuous rated load. Flag for review