Asked on: Tuesday, February 15, 2011 at 12:21 pm EST
Answered on: Tuesday, May 14, 2024 at 1:36 am EDT
Question: Can anyone tell me when it was first required (in the NEC) that the branches of the essential electrical system by separated from each other? I think it was 1999 but I don't have a copy of anything older than 2005. I have had several clients get frustrated when I tell them that to add a receptacle to the emergency system will require a complete rework of at least part of the there electrical system to get L&I approval.Thanks,Wes
In the 1999 NEC, Section 700.12(B) required that the emergency system be separated from all other electrical circuits700.12 Wiring.(B) Separation from Other Circuits.Emergency circuit wiring shall be kept entirely separate from all other wiring and equipment and shall not enter the same raceway, cable, box, or cabinet or other enclosure with other wiring except as permitted in 700.15(B), 700.24(\1), and 700.24(F). Flag for review