Question: I am an electrical contractor who specializes in mult-family projects. Recently, we have been wiring mixed-use and high-density apartment projects. These projects, unlike your typical garden style apartments, have significantly longer SER/subfeeder runs to the unit panels due to meterbase locations being more spread out. We typically use Square D EZM Modular Metering rated at 125 Amps, example, a Square D EZMR115125 (125 Amp-rated 5 Gang). Within this meterbase we install unit main breakers ranging up to 125 Amps, example, a Square D QO2125-VH (125 Amp 2 Pole, 22K AIC, Unit Main). These "QO" breakers have a maximum wire size of 2/0 AWG. Voltage Drop on long subfeeder runs sometimes require the use of conductors larger than 2/0. We have been told that 125 Amp-rated meterbases are not UL approved for any conductors larger than 2/0 AWG. However, we can find no documentation through Square D engineers or the UL White Book that proves or disproves this statement.I understand that there are certain products such as "MAC ADAPTS" and Ilsco reducing lugs that would reduce the wire size that terminates into the unit breaker. These would be installed in the wireway section of the meterbase and would allow a 4/0 AWG SER cable to be reduced to a 2/0 AWG and terminated under the unit breaker. Another option would be to increase the meterbase size to a 225 Amp that would require breakers that accept up to 300 KCMIL conductors. However, this set-up is very costly. Is there any restrictions on the maximum size of SER cable that can be installed in these meterbases that are rated 125 Amps?We are looking for the least cost-effective design that meets the National Electrical Code.
Answer
According to the UL White Book (UL 508), there is no specific restriction on the maximum size of SER cable that can be installed in a 125 Amp-rated meterbase. However, it is important to note the following:
Conductor Compatibility
The meterbase must be compatible with the size and type of conductor being used.
Wireway Capacity
The wireway in the meterbase must have sufficient capacity to accommodate the larger conductor size.
Terminal Capacity
The terminal blocks in the meterbase must be rated for the current carrying capacity of the larger conductor.
Voltage Drop
The voltage drop on long subfeeder runs must be calculated and accounted for to ensure that the voltage at the unit panel is within acceptable limits.
Cost-Effective Solution
The most cost-effective solution is to use a 125 Amp-rated meterbase with an appropriate wireway rating and install a conductor size that meets the voltage drop requirements. This may involve reducing the wire size at the unit breaker using reducing lugs or using a smaller unit main breaker.
Alternatives
MAC Adapts
MAC Adapts can be used to reduce the wire size at the unit breaker. However, they add cost to the installation and may introduce additional connection points.
Ilsco Reducing Lugs
Ilsco reducing lugs can also be used to reduce the wire size at the unit breaker. They are less expensive than MAC Adapts but may not be as reliable.*
225 Amp Meterbase
A larger 225 Amp meterbase would allow the use of larger conductors without the need for reducing lugs or smaller unit main breakers. However, this option is more expensive.
Conclusion:
While there is no specific restriction on the maximum size of SER cable that can be installed in a 125 Amp-rated meterbase, it is important to ensure that the meterbase, wireway, terminals, and voltage drop are all taken into consideration. The most cost-effective solution is to use a 125 Amp meterbase with an appropriate wireway rating and conductor size, potentially using reducing lugs if necessary. Flag for review