Topic: Additional service disconnect if panel is further than 5' from the meter

User: GeorgeKoehl, Location: Washington IL

Asked on: Tuesday, February 15, 2011 at 6:46 pm EST
Answered on: Tuesday, May 14, 2024 at 1:37 am EDT

Question: I have been looking for a code reference for a local rule here in Peoria IL.The inspectors here require an Service Disconnect if the panel will be more than 5 feet away from the meter.I can not find anything that specifically requires an additional disconnect means within 5 feet from the meter.The only code that I can find with any reference to location of Disconnect means is 230.70(A)(A) Location. The service disconnecting means shall be installedin accordance with 230.70(A)(1), (A)(2), and (A)(3).(1) Readily Accessible Location. The service disconnectingmeans shall be installed at a readily accessible locationeither outside of a building or structure or inside nearest thepoint of entrance of the service conductors.(2) Bathrooms. Service disconnecting means shall not beinstalled in bathrooms.(3) Remote Control. Where a remote control device(s) isused to actuate the service disconnecting means, the servicedisconnecting means shall be located in accordance with230.70(A)(1).

The requirement for a service disconnect within 5 feet of the meter in Peoria, IL, is a local rule. It is not a requirement of the National Electrical Code (NEC).Local rules are typically adopted by local municipalities to address specific safety concerns that are unique to their community. In this case, the local rule in Peoria, IL, is likely intended to reduce the risk of electrical accidents by ensuring that the service disconnect is easily accessible in the event of an emergency.If you are unsure about the requirements for your specific location, you should always consult with your local building inspector. Flag for review

Previous Question Next Question