User: Bruxley, Location: Fl
Asked on: Tuesday, February 15, 2011 at 8:17 pm EST
Answered on: Tuesday, May 14, 2024 at 1:38 am EDT
Question: I have a residence that has a 400 amp service. The service is split with 20 200amp breakers. One for the panel inside the main service and one to a 200amp panel on the opposite side of the house.Connected to the panel at the main service are 2 more subpanels of 125amps each on 125 amp breakers. I also have a 240v, 60amp AC connected to that same panel.An electrician told me I should have one of the 125amp subpanels moved to my other 200amp panel because 20 125amp panels on a 200amp rated bus is a code violation because the sum of the ratings of the subpanels cannot exceed the rating of the panel they are connected to and the sum of the ratings of all my subpanels cannot exceed the total service rating.This make sense? I does to me but I need a code citation. Any help?
NEC Citation
[NEC 408.21(A)]
Code Requirement
The sum of the ampere ratings of all overcurrent devices connected to any supply conductor shall not exceed the rated ampacity of the supply conductor.
Application to Your Situation
You have a 200-amp panel with 20 125-amp breakers. The sum of the breaker ratings (20 x 125 amps = 2,500 amps) exceeds the panel rating of 200 amps. Therefore, the configuration violates [NEC 408.21(A)].
Additional Considerations
The 125-amp breakers are connected to a 200-amp bus within the panel. The bus is not rated for the sum of the breaker ratings (2,500 amps). Therefore, the configuration also violates [NEC 110.14(A)].
Resolution: Move one of the 125-amp subpanels to the other 200-amp panel. This will ensure that the sum of the subpanel ratings does not exceed the rating of either panel and complies with [NEC 408.21(A)]. Flag for review