User: apbart, Location: Chapel Hill, NC
Asked on: Tuesday, February 15, 2011 at 11:18 pm EST
Answered on: Tuesday, May 14, 2024 at 1:38 am EDT
Question: I need alittle help in determining if the code will allow us to pull a solid #6 bare copper Grounding Electrode conductor inside a conduit with ungrounded and grounded current carrying conductors also inside of the same conduit? The inspector says that this is a code violation and refers to Article 310.3, which states that any conductor #8 or larger inside a conduit must be stranded, the exception to this, states that except as permited elsewhere in the code. Article 250.62 states a Grounding Electrode conductor shall be copper, aluminum, or copper-clad aluminum, solid or stranded, insulated, covered or bare. Would this be an exception to a conductor having to be stranded in a conduit ? We know that you can put a grounding electrode conductor in a metal conduit for physical protection. Is there any other code references that would allow or disallow you to put a solid grounding electrode conductor #8 or larger inside a conduit? Do you agree or disagree with the inspector?
Code Interpretation
Article 310.3 requires conductors #8 AWG and larger in a conduit to be stranded unless otherwise permitted elsewhere in the Code.Article 250.62 permits solid or stranded grounding electrode conductors.
Exception to Article 310.3
Article 310.3 provides an exception for conductors permitted elsewhere in the Code. Article 250.62 permits solid grounding electrode conductors, which would fall under this exception.
Additional Code References
Article 400.7(A): Grounding electrode conductors are not considered current-carrying conductors. Article 400.7(B)(2): Grounding electrode conductors can be installed in the same raceway, cable, or enclosure with other conductors.
Inspector's Interpretation
The inspector's interpretation that a solid #6 bare copper grounding electrode conductor cannot be installed in a conduit with current-carrying conductors is incorrect.
Conclusion
Based on the Code references cited above, it is permissible to install a solid #6 bare copper grounding electrode conductor inside a conduit with ungrounded and grounded current-carrying conductors.
Agreement with the Inspector:
I disagree with the inspector's interpretation. The Code clearly permits solid grounding electrode conductors in conduits. Flag for review