Topic: Floating pump station

User: sgunsel, Location: Olympia, WA

Asked on: Wednesday, February 16, 2011 at 10:14 am EST
Answered on: Tuesday, May 14, 2024 at 1:38 am EDT

Question: Industrial application is a floating platform (in pond) with 3 - 480 VAC TEFC motors in a Class I, Division 2 area. Motor controller will be on shore.Looks like Art 682 requires "all" electrical connections to be 30 inches above water level and 12 inches above deck level. I presume this includes the motor connections since the motors are not submersible.Can SOOW cord be used submerged from shore to the floating platform? If not, what would be a better choice?Thanks.

Electrical Connections Requirements

According to Article 682.8 of the National Electrical Code (NEC), all electrical connections on floating platforms in Class I, Division 2 areas must be located at least 30 inches above the water level and 12 inches above the deck level. This includes motor connections.

Submersible Power Connection

SOOW cord is not suitable for submersible use. It is a flexible, heavy-duty cord designed for temporary use in dry or damp locations, such as construction sites and workshops. Submerging SOOW cord can lead to electrical shock and electrocution.

Better Choice for Submersible Power Connection

For submersible power connections, the following cable types are recommended: Type W

Submersible thermoplastic insulated wire


Type G

Submersible rubber insulated wire*

Type A

Submersible armored cableThese cables are designed to withstand the harsh conditions of exposure to water and are suitable for use in Class I, Division 2 areas.

Conclusion


To ensure the safety of the electrical system on the floating platform, you cannot use SOOW cord for the submerged power connection. Instead, opt for a submersible cable, such as Type W, G, or A. Flag for review