Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Is this correct

User: jrvazzer, Location: 3 Hr 2 Min from Winged Horses

Asked on: Wednesday, February 16, 2011 at 11:41 am EST
Answered on: Tuesday, May 14, 2024 at 1:38 am EDT

Question: clients requested in their lease 400A 120/208v 3ph, 4w service for their facility. So you provide a 400A service. The question..... are they really getting 400A. Do they know that they are responsible for loading up their electrical needs to 80 percent of that breaker or fuse main. If the client was requesting 7 watts per sq. ft. and 400A met that and if their limited to 80 percent of the mains. Than actually they are getting 5.6 watt per sq.ft. Is that correct.sq. footage is 20571'.Thanks

Your calculations are incorrect.

Actual Amperage Available

A 400A service does not guarantee that the client is getting 400A. Electrical codes and standards require that the main breaker or fuse should be sized to handle 80% of the maximum load that the circuit can handle. In this case: Maximum amperage of 400A service = 400A 80% of maximum amperage = 0.8 400A =

320A


Therefore, the actual amperage available to the client is 320A, not 400A.

Actual Watts per Square Foot

Given the following information:
Requested wattage: 7 watts per sq. ft. Actual amperage available: 320A

Step 1: Calculate the total wattage available

Total wattage = Actual amperage Voltage Power factor Number of phasesAssuming a power factor of 1 and a 3-phase service: Total wattage = 320A 208V 1 3 =

215,040 watts
Step 2: Calculate the actual watts per square foot

Actual watts per sq. ft. = Total wattage / Square footage* Actual watts per sq. ft. = 215,040 watts / 20,571 sq. ft. =

10.46 watts per sq. ft.


Therefore, the client is actually getting 10.46 watts per square foot, not 5.6 watts per square foot. Flag for review

Previous Question Next Question