User: ptonsparky, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)
Asked on: Wednesday, February 16, 2011 at 3:52 pm EST
Answered on: Tuesday, May 14, 2024 at 1:40 am EDT
Question: I need to pull 20 circuits in about 4' of conduit including an LB. Ampacity due to conduit fill is a substantial reduction even for #10. Does replacing that LB with a box mid length, it is no longer one raceway but two of 24", get me by that minor detail?
No, using a box in the middle of the raceway does not get you by the conduit fill issue. The NEC still requires you to determine the ampacity of the conductors based on the total length of the raceway. In this case, it would be 4 feet. Flag for review