User: Nitty, Location: Tennessee
Asked on: Wednesday, February 16, 2011 at 4:28 pm EST
Answered on: Tuesday, May 14, 2024 at 1:40 am EDT
Question: I am moving some spot welding equipment and am questioning the present installation. Example; Spot Welder 480Volt, Single Phase, 150KVA, 80' from distribution panel. Presently it is being fed with 2) 500 KcMil Copper conductors and a 400 amp breaker. After reviewing NEC 630.31 It seems that the ampacity of the circuit conductors shall not be less than 50% of rated primary current, which means I could refeed the spot welder with 2/0awg Copper (175 amps) provided the distance wouldn't require voltage drop derating, and simply reuse the 400 amp breaker for overcurrent protection. Is there something I may be overlooking?
You are correct that according to NEC 630.31, the ampacity of the circuit conductors shall not be less than 50% of the rated primary current of the welder. However, you should also consider the voltage drop over the 80' length of the circuit.The voltage drop over a circuit can be calculated using the following formula:
Voltage drop = (Circuit length) x (Current) x (Resistance per unit length)For copper conductors, the resistance per unit length can be found in Table 8 of the NEC. For 2/0 AWG copper conductors, the resistance per unit length is 0.049 ohms per 1000 feet.Using the formula above, the voltage drop over 80 feet of 2/0 AWG copper conductors carrying 175 amps is:Voltage drop = (80 feet) x (175 amps) x (0.049 ohms per 1000 feet) = 6.86 voltsThis voltage drop is acceptable, as it is less than 5% of the welder's rated voltage (480 volts). Therefore, you could refeed the spot welder with 2/0 AWG copper conductors and reuse the 400 amp breaker for overcurrent protection.However, you should also check the voltage drop over the secondary circuit of the welder. The secondary circuit is the circuit that connects the welder to the workpiece. The voltage drop over the secondary circuit can be calculated using the same formula as above, but you will need to use the resistance per unit length of the secondary circuit conductors.If the voltage drop over the secondary circuit is too high, it can cause the welder to operate improperly. Therefore, you should make sure that the voltage drop over the secondary circuit is within the manufacturer's specifications. Flag for review