User: ElectricFuzz, Location: Fl
Asked on: Wednesday, February 16, 2011 at 7:07 pm EST
Answered on: Tuesday, May 14, 2024 at 1:41 am EDT
Question: Hi, I recently ran into a problem with an inspector. I had 2x2 flourescent fixtures mounted in a suspended ceiling. They were cord and plug connected above the ceiling with a 14 gauge SJT cable. The ceiling is a plenum ceiling. The inspector told me I could not do this. Why? I thought SJT was rated for plenum.
Plenum-Rated Cables
In plenum spaces, which are spaces within air-handling systems used for distributing conditioned air throughout a building, the use of specific types of cables is required to meet fire safety standards. Plenum-rated cables are designed to emit less smoke and release less corrosive gases when burned, minimizing the risk of damage to equipment and the spread of fire.
SJT Cable
SJT cable is a non-metallic, flexible cord commonly used for powering appliances, lamps, and other portable equipment. While SJT cable is rated for use in damp locations, it is not plenum-rated.
Reason for Inspector's Concern
The inspector raised a valid concern because using non-plenum-rated cables in a plenum ceiling is a violation of safety codes and fire regulations. In the event of a fire, non-plenum-rated cables can emit toxic gases and smoke, potentially endangering occupants and damaging equipment.
Acceptable Cables for Plenum
According to the National Electrical Code (NEC), only certain cables are permitted in plenum spaces. These include: Plenum-rated cables (identified with the letters "CMP") Metal-clad cables (such as Type MC)* Mineral-insulated cables (such as Type MI)Solution
To resolve the issue with the inspector, you must replace the non-plenum-rated SJT cable with a plenum-rated cable. This can be accomplished by pulling new wire through the existing conduit or by installing a new plenum-rated cable assembly. Flag for review