Question: sizing motor circuit protect: heat pump/supplemental electric heat & blower packageI need help sizing motor circuit protect: heat pump/supplemental electric heat & blower packageI have a new fan in the attic that draws about 2A 230v.I just found out that there is a supplemental electric heater [KFCEH0401N03] that draws 12a at 240v.There is a new package unit outside with compressor/fan that draws 16.1 FLA at 240v. It's a real 240v from a delta supply.My original idea was to use the old AC feed with existing 30a cb and put aGE manual motor starterwith the16a heater in itas a local disconnect and wire the whole thing in #10. I was going to use another manual starter at the blower with a two amp heater in it, also wire it in #10.The CBs protecting the whole thing are very old too I must say.First, I don't know if that idea would've been ok because I can't continue because the supplement heat is now to be provided for.Anyway, now I have to run another circuit back to the old main and get a blower/heater 2p ct.Is my original idea ok for the package unit, that is to have it under the 30a 2p, run it using the old #10's and then disconnect the unit with a local [toggle] manual motor starter that has a 16a heater strip for protection?Can I downgrade my blower disconnect to simply a two pole 20a toggle on my new 20a 2p circuit for the blower and sup heat? Downgrade, that is, because of no fuse.Usually these things have fused disconnects next to them, but when I sized the needs, this seemed adequate. Am I missing something because the original breakers are not HVAC rated? Or because the breakers are sized for the wire but I have to interrupt the load from the disconnect with breakers sized at 125% to allow for inrush or locked rotor?At the blower/heater, since it is just a squirrel cage, there doesn't seem too much chance of it locking up. It seems not much different from the blower on a FAU that is just protected by a summer switch.Thanks Guys!
Motor Circuit Protection for Heat Pump/Supplemental Electric Heat & Blower Package1. Package Unit The package unit draws 16.1 FLA at 240V. According to NEC 430.52, the motor branch circuit should be protected at 250% of the FLA for compressors. Therefore, you need a circuit breaker or fuse rated at 250% x 16.1 FLA = 40.25 FLA or 41 Amps. You can use a 40 Amp circuit breaker with a 16 Amp heater strip in the motor starter. The #10 wire is sufficient for this circuit.2. Blower and Supplemental Electric Heater The blower draws 2 Amps at 230V. The supplemental electric heater draws 12 Amps at 240V. The combined load is 14 Amps at 240V. According to NEC 430.52, the motor branch circuit should be protected at 125% of the FLA for general-purpose motors. Therefore, you need a circuit breaker or fuse rated at 125% x 14 Amps = 17.5 Amps or 18 Amps. You can use a 20 Amp circuit breaker with a 2 Amp heater strip in the motor starter for the blower. The #10 wire is sufficient for this circuit.3. Disconnect Switches Manual motor starters are acceptable as local disconnects. They should be rated for the full-load current of the motor they protect. In this case, you can use a 16 Amp manual motor starter for the package unit and a 2 Amp manual motor starter for the blower.4. Circuit Breakers The original circuit breakers are not HVAC rated, which means they may not provide adequate protection for the high inrush currents of HVAC equipment. It is recommended to replace them with HVAC-rated circuit breakers. The circuit breakers should be sized at 125% of the FLA for the motor they protect.5. Summary of Protection Package Unit: 40 Amp circuit breaker with 16 Amp heater strip in motor starter Blower and Supplemental Electric Heater: 20 Amp circuit breaker with 2 Amp heater strip in motor starter Manual Motor Starters: 16 Amp for package unit, 2 Amp for blowerNote: All wiring should be installed in accordance with the National Electrical Code (NEC) and local codes.* It is always recommended to consult with a qualified electrician for proper sizing and installation of equipment. Flag for review