Question: So what little of the Code I know something about includes "in sight disconnects" meaning motors must have such right there. I think that is 430.102.But it occurs to me that I have seen many residential well pumps, 30-600 ft down, and none had such. Why is that? Is there some exception that applies? I ask because that VFD I recently discussed is for one; the VFD will be inside and not in sight.Will a lockable breaker feeding the VFD be sufficient?
430.102 - Disconnecting Means Location
You are correct that Section 430.102(B)(1) of the National Electrical Code (NEC) requires motors to have a disconnecting means that is "within sight from the motor location". This is to allow for quick and easy disconnection of the motor in case of an emergency.
Exception for Well Pumps
However, there is an exception to this requirement for well pumps. Section 430.102(C) states that:> "Disconnecting means shall not be required to be within sight from the motor location if the motor is located more than 30 ft (9.1 m) underground in a well."This exception applies to well pumps because they are typically located deep underground and it would be impractical to install a disconnecting means within sight of the motor.
Lockable Breaker
In your case, where you have a VFD for a well pump that will be located inside and not in sight of the motor, a lockable breaker feeding the VFD would be sufficient as a disconnecting means. This is because it would allow you to quickly and easily disconnect the power to the motor in case of an emergency, even though it is not within sight.
Summary The general rule is that motors must have a disconnecting means that is within sight from the motor location. There is an exception for well pumps that are located more than 30 ft underground in a well.* In your case, a lockable breaker feeding the VFD would be sufficient as the disconnecting means for the well pump motor. Flag for review