User: DisconnectingMeans, Location: Utah
Asked on: Wednesday, February 16, 2011 at 11:49 pm EST
Answered on: Tuesday, May 14, 2024 at 1:42 am EDT
Question: Pop Quiz:You come across a panel with both the neutral and grounding conductors terminated on the neutral bus bar. The grounding conductors are all bonded to each junction box in the existing piping system that supplies all utilization equipment and outlets. The panel itself has a jury-rigged bond to the building steel but its straight to the panel can, with no connection to the neutral bus... How bad is this?
This is a serious violation of the National Electrical Code (NEC) and poses a significant safety hazard.
Reasons why this is bad
Neutral-Ground Bond
The neutral and grounding conductors should not be bonded together on the neutral bus bar. This is because the neutral conductor carries both the current from the phase conductors and the current from the grounded equipment. When these currents flow through the same conductor, it can cause voltage fluctuations and increase the risk of electrical shock.
Grounding Electrode Connection
The grounding conductors should be connected to a grounding electrode system, which typically consists of a ground rod, a water pipe, or a building steel frame. This connection ensures that any fault currents or lightning strikes are safely dissipated into the earth. In this case, the grounding conductors are only bonded to the junction boxes, which are not a suitable grounding electrode.*
Improper Panel Bonding: The panel has a jury-rigged bond to the building steel, but it does not have a direct connection to the neutral bus bar. This means that the panel is not properly grounded, and there is no path for fault currents to flow back to the source. This can lead to an increased risk of electrical shock and fire.Overall, this configuration is highly unsafe and should be corrected as soon as possible by a qualified electrician. Flag for review