Question: trying to find the refrence for installing the neutrals and ground wires on the same bar in a residential panel with main cb that serves as the service entrance equipment.

National Electrical Code (NEC)Article 250.24(A)(5)2020 NEC

> "Grounding and bonding equipment shall be connected to the grounding electrode conductor or the equipment grounding conductor where one exists. Where an equipment grounding conductor does not exist, grounding and bonding equipment shall be connected to the grounded conductor of the circuit at the service, disconnecting means, or overcurrent device."

Interpretation:


This code section requires that neutral and ground wires be connected to the same grounding electrode conductor or equipment grounding conductor. In a residential panel with a main circuit breaker (MCB) that serves as the service entrance equipment, the MCB's neutral terminal and grounding terminal are typically connected together, providing a common point for the connection of both neutral and ground wires. Flag for review