Question: I am installing a 3ph contactor on a motor load. It is used as an auxilary control to shut down a car wash. it will not be used under load or to start and stop the car wash. All normal disconects and starters are allready in place. It will be used for conveince so the single employee does not have to leave the store to turn off the carwash when temps drop. How do I size this contactor? As a disconect? Just off the nameplate?Thanks
Sizing the Contactor for Non-Load Switching
Since the contactor will not be used for load switching (starting or stopping the motor), it can be sized based on the motor's full-load current (FLA) and not the starting current.
Steps to Size the Contactor
1.
Determine the Motor's Full-Load Current (FLA)
Refer to the motor nameplate or consult the manufacturer's specifications.2.
Select a Contactor Rating
Choose a contactor rated for a current that is at least equal to or slightly higher than the motor's FLA. For example, if the motor's FLA is 25A, select a contactor rated for 30A or higher.
Additional Considerations
Voltage Rating
Ensure the contactor's voltage rating matches the supply voltage of the motor.
Enclosed or Open Contactor
If the contactor will be installed in a dusty or wet environment, consider using an enclosed contactor for protection.
Auxiliary Contacts
If additional control functions are desired, such as providing status indication or triggering alarms, select a contactor with auxiliary contacts.
Sizing Example: Motor FLA: 25A Suitable Contactor Rating: 30A or higher Voltage Rating: 480V Required Contact Type: 3-phase, normally open (NO) Additional Contacts: None requiredBased on this information, you would select a 30A-rated, 480V, 3-phase NO contactor without additional contacts. Flag for review