Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: tray cable into conduit

User: ejb1556

Asked on: Thursday, February 17, 2011 at 12:59 pm EST
Answered on: Tuesday, May 14, 2024 at 1:43 am EDT

Question: I have been looking but saw nothing that really satisfied my question in the nec. If I use 3 conductor tray cable and then enter conduit through a cgb, can I strip off the outer sheath leaving the three xhhw conductors to run through the conduit? It will have an epoxy seal prior to terminating at a device.

Yes, you can strip off the outer sheath of a 3-conductor tray cable and run the XHHW conductors through a conduit.NEC References



Article 336.10(7)
: "Where cables enter a raceway, the cable sheath shall be stripped back a sufficient length to provide an approved seal." Section 336.10(6): "Conductors entering enclosures from raceways shall be protected by approved bushings."Procedure

1. Strip the outer sheath of the tray cable back to the point where you want the conductors to enter the conduit.
2. Install an approved bushing or sealing fitting on the conduit entry point.3. Pull the XHHW conductors through the conduit and into the enclosure.
4. Apply an epoxy seal around the conductors where they enter the conduit.5. Terminate the conductors according to the requirements of the applicable NEC sections.


Note:
The epoxy seal must be approved for the type of cable and conduit being used. The bushing or sealing fitting must be listed and approved for use with the type of tray cable and conduit being used. Flag for review

Previous Question Next Question