Question: When a transformer is located above a suspended ceiling (45Kva) can the secondary OCPD be located in the ceiling space adjacet to the xfmr.? Or does it have to be located below the ceiling?
The secondary OCPD can be located in the ceiling space adjacent to the transformer. Flag for review