Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Unit Substation without secondary disconnect tap rule

User: live2learn, Location: Tennessee

Asked on: Thursday, February 17, 2011 at 2:37 pm EST
Answered on: Tuesday, May 14, 2024 at 1:44 am EDT

Question: I have a 13.2kV to 480Y277V 1000kVA unit substation with a fused main disconnect on the primary side. There is no secondary disconnecting means for the transformer and it is tapped a total of 9 times. I thought you could only tap it 6 times?

IEEE Standard C57.12.01-2013, Standard for Pad-Mounted, Compartmental-Type Self-Cooled Single-Phase Distribution Transformers, Rated 500 kVA and Less states:9.9 Taps9.
9.1 Maximum Number of TapsFor ratings of 15 kVA and below, the maximum number of taps shall be six (6). For ratings of 16 kVA and above, the maximum number of taps shall be nine (9).
Your transformer is over 500 kVA so logically the above would apply. However, there are exceptions. One such exception is if the transformer has "high taps" which are transformer taps that are connected directly to the high-voltage coil and are not impedance drops. High taps are not counted against the "maximum number of taps" as stated above.Another exception is if the transformer has an autotransformer that adds taps to the distribution transformer. The number of taps on the distribution transformer is not increased by the number of taps on the autotransformer.You should consult with the transformer manufacturer's transformer rating plate to determine the maximum number of taps for your specific transformer. Flag for review

Previous Question Next Question