Topic: Medium Voltage unit substation secondary tap rule

User: live2learn, Location: Logan, Utah

Asked on: Thursday, February 17, 2011 at 2:58 pm EST
Answered on: Tuesday, May 14, 2024 at 1:44 am EDT

Question: I have a unit substation that is 13.2kV 1000kVA to 480Y277V. This is an existing installation with a fused disconnect on the primary side and no disconnect on the secondary side of the xfmr. With that said the secondary of the xfmr hits a bus and that has 9 circuit breakers that feed typical loads.The primary is controlled by a fused disconnect switch. Would the tap rule come into to play and limit me to only 6? Would the MV cable be considered my service entrance feeder and my fused disconnect switch be the building disconnecting means? The substation is owned by the owner. This is in a supervised location.

Tap Rule

The tap rule applies when a step-down transformer has multiple secondary feeders. In this case, the secondary bus with 9 circuit breakers would be considered multiple secondary feeders.The tap rule states that the rating of the overcurrent protective device on any transformer secondary feeder must not exceed 125% of the ampacity of the feeder. This means that the overcurrent protective device on each circuit breaker would need to be rated for less than 125% of the ampacity of its associated feeder cable.

Service Entrance Feeder and Building Disconnecting Means

The MV cable from the utility distribution system to the unit substation would typically be considered the service entrance feeder. The fused disconnect switch on the primary side of the transformer would likely serve as the building disconnecting means.

Application to Your Situation

In your case, it is not clear whether the tap rule would limit you to only 6 circuit breakers on the secondary side of the transformer. This would depend on the ampacity of the feeder cables and the ratings of the circuit breakers.

Recommendations

To determine the applicability of the tap rule and the suitability of the existing configuration, it is recommended that you: Determine the ampacity of the secondary feeder cables. Verify the ratings of the circuit breakers on the secondary bus. Consult with a qualified electrical engineer or electrician to ensure compliance with applicable codes and standards.

Additional Considerations:
Supervised locations typically require some level of code compliance, so the existing configuration may need to be modified to meet code requirements.* The owner of the substation should have a maintenance agreement in place to ensure proper operation and maintenance of the equipment. Flag for review