Topic: Anodize Rectifier hook-up Article 669.5

User: Davebones, Location: North Of Tampa Fl

Asked on: Thursday, February 17, 2011 at 3:19 pm EST
Answered on: Tuesday, May 14, 2024 at 1:44 am EDT

Question: We have a new rectifier to hookup in our Anodize area . 100 amps at 480V on the nameplate .669.5 says branch circuit conductors SHALL have a ampacity of not less than 125% of the total connected load . ( 100 amps x 125% = 125 amps ) Do we also have to up the size of the breaker that feeds this ????? This is not a continuous load ..

Yes, you also need to up the size of the breaker that feeds the rectifier.According to NEC 430.24(A), the branch-circuit conductors shall have an ampacity of not less than 125% of the total connected load. In this case, the total connected load is 100 amps, so the branch-circuit conductors must have an ampacity of at least 125 amps.The overcurrent protection device (breaker) must also be sized to protect the conductors. According to NEC 240.4(B), the ampacity of the overcurrent protection device shall not exceed the ampacity of the conductors. Therefore, the breaker that feeds the rectifier must have an ampacity of at least 125 amps.It is important to note that the ampacity of the conductors and the breaker must be based on the full-load current of the rectifier, even though it is not a continuous load. This is because the conductors and breaker must be able to handle the maximum current that the rectifier can draw. Flag for review