Topic: Branch breaker kAIC rating

User: sbutler, Location: North Charleston, SC

Asked on: Thursday, February 17, 2011 at 3:43 pm EST
Answered on: Tuesday, May 14, 2024 at 1:44 am EDT

Question: I thought the code required branch breaker ratings to be the same or more than the main but cant find it.Thanks for any feedback.

National Electrical Code (NEC) 240.15 requires that the branch-circuit short-circuit current rating be equal to or greater than the main circuit short-circuit current rating. Flag for review